Not necessarily so.
We did quite a few paoer mills with 12 and 24 pulse systems. The largest, as I recall, is a 4MVA system with 17 variable speed drives. The drives were a mixture of DC, DC 4-quad and some variable frequency inverters.
The system comprised two 2MVA 11kV/520V transformers, four six pulse plain rectifiers, and a 700Vdc busbar distribution system with all the drives hanging off that.
Lowest order harmonic is 23rd and, as you know, harmonic amplitude is roughly proportional to the reciprocal of the harmonic number. The arrangement has benefits on system efficiency but that's another story for another day.