georgeswe
- The Republic of Southern California
I know this topic has been brought up in many now closed threads but I would like to put my 2 cents worth in on the topic.
Being in the office now and out of the field for a bit now I have not had to deal with this issue directly, but I did do some homework to make sure we are covered as a company.
As a whole we have been mounting our switches at 48" to the top of the junction box and receptacles 18" to the top of junction box in an office environment.
I know that the ADA guidelines set in ADA's accessible designs documents call for devices or controls to be mounted above 15" and below 48" A.F.F.
NECA-1 on 110.12 calls for 48" for switches and 18" for receptacles measured to the center of the device.
Well the 28 CFR part 36 ADA Standards for Accessible Design states that the measurement for these devices will be between 15" and 48" AFF to the operable part of the device.
So if you were to use as we do 18" to the top of box for receptacle location technically the bottom of a duplex receptacle would be bellow the 15" - "operable part” of the receptacle.
This is important because these issues spawn lawsuits and they DO get very technical.
I think since our switch box is mounted at 48" to the top we are ok there but if you were to use the 48" to the middle of the box as set in the NECA book you could possibly have issues there too.
I will be having a foreman’s meeting and we will be changing our general mounting heights to 20" to the top of an outlet/phone locating box to avoid any future issues. Taking into account for carpet and tile when roughing in on our jobs.
Just checking what you guys think on the subject???
The attached image is from NECA book