Add Ground lugs to GE PowerMark Gold

Status
Not open for further replies.

lanel

Member
Location
ga
Occupation
Electric Utility Electronics Specialist
I have a GE PowerMark Gold wired as a subpanel in our house which will feed another 125A subpanel at a poolhouse. I need to add 2/0 ground lugs to both the neutral bar and the ground bar. I picked up a GE lug with the tabs that insert under the screws in the existing ground and neutral bars but the width of the tabs are too wide to get into the screw holes. The holes are approx 3/8 oc.

One option I have considered was using a dual ground lug that screws down from the top. The other is the one above with the two tabs that are placed under the screws in the existing ground/neutral bars. I have not been able to find any compatible with what I have. They need to accept 2/0 and be sufficient for a 125 amp circuit.

Can anyone offer suggestions as to the best method to use and provide part numbers/sources for what I need. I was going to contact GE but they are so large that I could not find a contact for the electrical panel division.

Thanks,
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
You can access "GE Buy Log Load Centers" on line. There is an accessory section where you can compare with what you have.
(Often the load center cover data sheet will have that info)
 

lanel

Member
Location
ga
Occupation
Electric Utility Electronics Specialist
Why do you have a 2/0 neutral and especially a 2/0 ground in a 125A rated panel?
I have a direct burial quad cable and the ground I believe is 1/0. Other conductors are 2/0

When the subpanel was installed many years ago it was only intended to provide some expansion for the house. It has very little loading on it so changing it out would be an option since it will now need to feed another subpanel in a pool house.
 

lanel

Member
Location
ga
Occupation
Electric Utility Electronics Specialist
load center cover data sheet
I have all the info from the label. I tried to find the lugs listed and did not see them online. It may be that the panel is obsolete. But I will check into the site you mentioned. Thanks
 

kwired

Electron manager
Location
NE Nebraska
I have a direct burial quad cable and the ground I believe is 1/0. Other conductors are 2/0

When the subpanel was installed many years ago it was only intended to provide some expansion for the house. It has very little loading on it so changing it out would be an option since it will now need to feed another subpanel in a pool house.
Do you even have room for those conductors in the panel?

How about some sort of tap connector on the feeder conductors?
 

lanel

Member
Location
ga
Occupation
Electric Utility Electronics Specialist
This is a picture of what I am working with. On the ground bar (left) I wanted to add a lug at the top and move the current bonding wire down wot accommodate. On the neutral bar (right) there is already an occupied lug from the main panel neutral. I need to add another lug there. I had looked at a dual stacked type that would mount on top.

Like I said, it is lightly populated so changing out the entire panel to a larger one could be an option but if I can make this properly work, that would be my preference since I would not expect to be adding much of anything else later on.

I am not familiar with the tap you are talking about. What does it look like?

IMG_1303.jpg IMG_1304.jpg IMG_1302.jpg 66750563632__3D349BDE-36BD-4BED-A4B2-2CF9536B6521.jpg
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
From my local Home Depot, all GE parts, in no particular order:





The first one has a very high price, but it might be for a 10-pack.
 

kwired

Electron manager
Location
NE Nebraska
I am not familiar with the tap you are talking about. What does it look like?
Many options, split bolt, crimp on, mechanical lug types, Polaris type taps....Just make a tap to the feeder conductor if you can't find some sort of adapter for neutral/ground bus or if they are full.
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
What's with all the Green? The ungrounded and grounded conductors are a violation of 250.119 in using the green conductors on these. There is no allowances for reidentifying of the grounding conductor for any other purpose other than the grounding conductor.
 

lanel

Member
Location
ga
Occupation
Electric Utility Electronics Specialist
I
From my local Home Depot, all GE parts, in no particular order:





The first one has a very high price, but it might be for a 10-pack.
Thanks for the information. The way things have gone up and the shortages, maybe it is for one? I went back and looked at what cable I purchased and it is not 2/0, it's (3) 1/0 with a #4 ground. But I still have to find a way to connect additional wiring.
 

lanel

Member
Location
ga
Occupation
Electric Utility Electronics Specialist
What's with all the Green? The ungrounded and grounded conductors are a violation of 250.119 in using the green conductors on these. There is no allowances for reidentifying of the grounding conductor for any other purpose other than the grounding conductor.
I will end up changing out the green wiring to a slightly larger gauge. But I have an electrician friend who said the wires could be re-identified. Are you saying the greens being re-identified for the hots are OK, just not on the ground and neutral? Thanks
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
I will end up changing out the green wiring to a slightly larger gauge. But I have an electrician friend who said the wires could be re-identified. Are you saying the greens being re-identified for the hots are OK, just not on the ground and neutral? Thanks
No, read the code referenced, it does not allow green for any other purpose other than for grounding. Larger black wires can be re-identified for grounded or grounding conductor, but code does not allow for green to be re-identified. White in the case of a cable assembly only, is allowed to be re-identified as an ungrounded conductor.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Sorry to have to do this but Forum rules say we can't help DIY installations unless you are an electrician.
I would suggest you have an electrician help with this project. One that is familiar with the code.
 