The only reason I would is because an inspector in town told me once "just make everything above ground sch 80" and it's a rule I've stuck to.I know it's questionable but I would use sch 40, I just don't see the need for sch 80
I would use a PVC offset nipple with a terminal adapter.
I'm sure that's fine as well. This is a heavy ag area, it's technically a house on an orchard, so, it's not like it's downtown Los Angeles.I would use a PVC offset nipple with a terminal adapter.
Sealing locknuts are fairly effective, but just like myers hubs AFAIK are only listed for use with RMC/IMC.and use a Meier hub regardless if the threads aren’t correct it’s better than the stupid sealing lovknuts
I think this is great feedback, thank you.3r Gutter solves all your issues for future panel placement, not having to worry where the underground feeder pipes stub up, and, not having to run into the same problem your fixing to have feeding that disconnect whatever its for, but that's jus me.
Jap>
View attachment 2579766
Yes, if the entry is above live parts you'll need a fitting listed for wet locations.I assume I can use EMT and raintight compression connectors, and avoid myers hubs?
Yes for the panel they're below live parts but what about entering the wireway? Those would be required to be listed for wet locationsIs there any reason to not just use PVC where I have the red arrow? They'd all be below live parts
Heads up though sealing locknuts are only good for imc, rmc or liquidtight connectors per the ul listingAnd if you do go above energized parts, use a Myers hub or sealing locknuts.
still rather used pvc to Myers inspector don’t bark at the thread mismatch- it seals better than sealing nuts- and is that not are job to make it safer

If that 2" nipple in the botttom of the panel is to get the feeder from the Tenant Main to the Panel, where's the nipples back into the gutter from the panel to get the future branch circuits back out of it?
Also,
Before the wire is pulled, what it the 2nd tenant Main for in the Meterpack?
If to feed a future panel at the left end of the rack, It's not too late to move the gutter to the right a few inches, install the nipples now, and, cover all the future needs.
Oh well, not sure of the future scenario.
View attachment 2579784
I also hope it's not the intent to pull multiple branch circuits from the panel through the 2" conduit to the building.
Jap>