trevorm
Member
- Location
- Central Washington
- Occupation
- Electrician
Hi Folks,
I'm doing a load calc to see if I can add an welding outlet and a EV charger to a single family dwelling. I was unsure how to add these in with the optional method but found good info here. Now the part i'm confused with is how to add in the 10kw space heater in the garage to the calculation. There is a central forced air heating system with supplemental electric heating included at 100% of compressor and 65% of supplemental heating.
I've added the 10kw garage heater at 65% on top of this but i don't think that is correct. Although if i follow 220.82(C) I would possibly omit the smaller of these two heat sources? Doesn't seem right since this heater is heating a difference space. Maybe i should try the standard method. Here are my full calculations for reference:
Obviously this is too much load for the service but I'm trying to figure out if there is enough space left to add the welding outlet and then wire the EV charger through a energy management system such as the stepwise tap.
I'm doing a load calc to see if I can add an welding outlet and a EV charger to a single family dwelling. I was unsure how to add these in with the optional method but found good info here. Now the part i'm confused with is how to add in the 10kw space heater in the garage to the calculation. There is a central forced air heating system with supplemental electric heating included at 100% of compressor and 65% of supplemental heating.
I've added the 10kw garage heater at 65% on top of this but i don't think that is correct. Although if i follow 220.82(C) I would possibly omit the smaller of these two heat sources? Doesn't seem right since this heater is heating a difference space. Maybe i should try the standard method. Here are my full calculations for reference:
Obviously this is too much load for the service but I'm trying to figure out if there is enough space left to add the welding outlet and then wire the EV charger through a energy management system such as the stepwise tap.
Fixed Appliances and Equipment | Load (W) |
Square Footage @ 3VA x 2252 | 6756 |
small appliance circuits(2) | 3000 |
laundry circuit | 1500 |
range (nameplate) | 12500 |
dryer (nameplate) | 6240 |
water heater (nameplate) | 4500 |
dishwasher (nameplate) | 1071 |
microwave (nameplate) | 1200 |
Hot tub 40A 240V (nameplate) | 9600 |
Welder Receptacle 50A 240V (NEW) | 12000 |
EV Charger 60A 240V | 14400 |
| |
Total before demand factor | 72767 |
First 10000 @ 100% | 10000 |
Remaining @ 40% | 25106.8 |
Total with demand factor | 35106.8 |
| |
Heating Loads | |
Heat pump compressor @ 100% 18.3A x 240V | 4392 |
Backup heat @ 65% = 40A+20A x 0.65=39A x 240V | 9360 |
Garage heater @ 65% = 10000x0.65 | 6500 |
Total heating loads | 20252 |
| |
Total demand+total heating (W) | 55358.8 |
Total Service Load in Amps | 230.7 |