Trying to wrap my head around the 120% rule in this case.
Specifically, by adding 40A, is there a risk of overloading feeder conductors or sub panel?
My question pertains to how the Back Up Interface works. That confuses me.
Background:
Existing SolarEdge PV+BATT system from 2020/2021.
-SolarEdge Energy Hub 7600 INV
-LG 16 kWH DC battery
-SolarEdge Backup Interface (BUI)
(See inline image, also attached as file)
Plans:
We want to add about 9.6 kW of PV.
Logical choice seems to be to pair it with a SolarEdge Energy Hub 7600 inverter.
How can i do this so I don't overload any existing feeder conductors, and in a Code compliant matter?
Specifically, I am forgetting how the SolarEdge BUI (Back Up Interface) works.
As you can see I simplified what the BUI does on the SLD below.
Can I add 40A of inverter output to the BUI?
(it can take 3@40A)
I.e. is that going to add to the (E) 40A of PV plus the (E) 110A from main breaker upstream and then feed 40+40+110A (190A) to the (E) 125A rated sub panel?
(shouldn't, right?.... because then the (E) 40A+110A (150A) would be a problem already)
Otherwise, I am fairly confident we are good vis a vis the MSP.
( It is a MBO main brkr. only panel, so no distribution and no busbar, so no 120% rule.)
Specifically, by adding 40A, is there a risk of overloading feeder conductors or sub panel?
My question pertains to how the Back Up Interface works. That confuses me.
Background:
Existing SolarEdge PV+BATT system from 2020/2021.
-SolarEdge Energy Hub 7600 INV
-LG 16 kWH DC battery
-SolarEdge Backup Interface (BUI)
(See inline image, also attached as file)
Plans:
We want to add about 9.6 kW of PV.
Logical choice seems to be to pair it with a SolarEdge Energy Hub 7600 inverter.
How can i do this so I don't overload any existing feeder conductors, and in a Code compliant matter?
Specifically, I am forgetting how the SolarEdge BUI (Back Up Interface) works.
As you can see I simplified what the BUI does on the SLD below.
Can I add 40A of inverter output to the BUI?
(it can take 3@40A)
I.e. is that going to add to the (E) 40A of PV plus the (E) 110A from main breaker upstream and then feed 40+40+110A (190A) to the (E) 125A rated sub panel?
(shouldn't, right?.... because then the (E) 40A+110A (150A) would be a problem already)
Otherwise, I am fairly confident we are good vis a vis the MSP.
( It is a MBO main brkr. only panel, so no distribution and no busbar, so no 120% rule.)