Rule 3. Additions or modifications to an existing installation shall be made in accordance with this Code without bringing the remaining part of the installation into compliance with the requirements of this Code. The installation shall not create a violation of this Code, nor shall it increase the magnitude of an existing violation.
romeo said:Contractor doing minumum housing work adds recpectical outlets to a exising 2 wire receptical outlet witout ground in a bedroom and installs gfci protection for the new outlets.
Help me with the NEC violatins
Jim W in Tampa said:Code would not only require the ground but also afci protection,so while its a nice attemt to make things safer it still falls way short of code.Are you a home inspector or electrical inspector ? Also lots depend on what code year was used at the time as well as local laws.
racerdave3 said:AFCI protection on an exisiting bedroom circuit? I question that one, again because it is EXISTING. I know we can sit here and debate this, and of course the AHJ will have the final say, but if it were a new installation, of course you would need the AFCI protection, but not on wiring that is already in place. I guess what comes to mind is the AFCI requirement they had put in the code that said you needed to put AFCI breakers in when you did a service upgrade, but later recinded it.
bhwolf said:Anything added must be protected. Since you're coming off an existing non-grounded circuit, do you then put a GFCI on the first new receptacle and an AFCI breaker in the panel?