Under the 2017 code, is there any rule prohibiting running a dedicated 15A circuit in a garage if the 20A requirement has been met?
Additional branch circuits rated 15 amperes or greater shall be permitted to serve receptacle outlets other than those required by 210.52(G)(1).
While clarification is certainly good, any such inspection authority was poorly versed in logical reading.There was some confusion on the application of the language in 210.11(C)(4) in the 2020 code with some inspection authorities reading that section as prohibiting additional non-20 amp circuits.