Hello,
I have a residence with an exterior main disconnect feeding an interior subpanel 30 feet away via a 4 wire cable, SER #1/0 Al. At the main disconnect is the usual grounding electrode system consisting of a Ufer ground, a driven ground rod, and the metallic water service. At the subpanel there is an additional Ufer ground available. Can this additional Ufer ground be connected to the subpanel's ground bar? Or can it only be utilized by running a separate bonding conductor back to the main disconnect? FWIW, the subpanel Ufer ground is part of a basement footing, while the main disonnect Ufer ground is part of a shallow footing.
Thanks, Wayne
I have a residence with an exterior main disconnect feeding an interior subpanel 30 feet away via a 4 wire cable, SER #1/0 Al. At the main disconnect is the usual grounding electrode system consisting of a Ufer ground, a driven ground rod, and the metallic water service. At the subpanel there is an additional Ufer ground available. Can this additional Ufer ground be connected to the subpanel's ground bar? Or can it only be utilized by running a separate bonding conductor back to the main disconnect? FWIW, the subpanel Ufer ground is part of a basement footing, while the main disonnect Ufer ground is part of a shallow footing.