Let me back up a bit.
wwhitney said:
Reading this, I have no idea what "individually" means.
What else can it mean, aside from multiple GECs? This is important, because it's not just a "the/a vs. them/some" singular/plural use of language - it is a specific and deliberate concept they are trying to communicate to the user of the code.
In any event, 250.64(F) uses the "shall be permitted" language, so it is not imposing a requirement, it is weakening one.
I see it as a sort of guarantee. The presence of "shall be permitted" language is not saying that it's lessening another rule; it's just saying that of the multitude of different ways of getting the job done, this handful shall not be questioned.
Can you point to a code section that requires more than one GEC? Or that requires all conductors in the GES terminating at the service grounded conductor to be a GEC?
What I look to is 250.53(C):
250.53(C) Bonding Jumper. The bonding jumper(s) used to connect the grounding electrodes together to form the grounding electrode system shall...
I read this to state that if a conductor starts and ends at an electrode, it is a bonding jumper.
What do you think about the use of the definite article in the definition of Grounding Electrode Conductor in Article 100?
I think the same as the definition of EGC just above it. I know there can be more than one EGC. One is the minimum, but I can add to that if I desire and it still must conform to the rules governing EGCs if I would like to use it as such.
The definition of GEC is consistent with the "service on one end, GE on the other" concept, IMO. I think it's also consistent with what I remember seeing of handbook diagrams as well.
So, I'm losing track - are we being purely rhetorical here, or have you actually broken a conductor that starts at the service, ends at a GE, and called it a bonding jumper and had it approved? I don't mind either way, just curious.