For an existing residence there is an existing underground fed 200A service panel which is located at the garage. I will be installing an additional flush mounted 200A service panel (meter/main) adjacent to it for other loads (AG) on the property. For the poco service lateral I will install a surface mounted 400A bussed termination enclosure with flex out the back of it for the service conductors to both panels. Here's the question: since the flex will penetrate the garage wall and travel a short distance inside the garage (probably less than 3' to both panels), will this be in violation of 230-3? ('99 NEC)