Re: addtional ground fault protection in hospitals
Yes, if the main breaker (i.e. one on the service) in a hospital has GFCI, the next set of breakers downstream must have GFCI. The idea is that a fault on one of the feeders is less likely to shut down the whole hospital. See 517.17.
Steve