I have a application on an industrial machine where a 200hp ASD is being used w/ a 100hp motor. The existing branch circuit protection is sized according to motor (fusing @ 175%FLA, wiring @ 125%FLA, and disconect @115%FLA). The reason for the 200hp drive is due to service factor motor is used at.
My question would be if the existing protection is properly rated to handle motor HP, should it stay as is or change based on ASD HP rating???