A 30 HP continuous-duty motor (460/3/60/40 FLA) is drive (w/integral pypass) supplied. I believe that if a NEMA 3 FVNR starter were used it would be permissible to protect the #6's selected with a 90/3 standard rated breaker.
It seems that the drive, however, would require #3's to be afforded protection by that same 90/3 breaker.
Any code thoughts or industrial experience on this topic is appreciated. gb_