Hi,
I have an interesting scenario. I have an existing installation of a square d 800A breaker (480V, 3P) that is 100% rated and in a substation all rated for 100%. We wanted to install parallel sets of 600 kcmil conductors in order to utilize the full 800A (using 90 degree C wire but sizing based on 75 degree C column). However, we recently found out the existing wire is parallel sets of 500 kcmil (THHN) and the client does not want to do a shutdown to upgrade the wire size. We have to temporarily adjust the long time pick up to 760A in order to protect the 500 kcmil wire (change to 600 kcmil at a later date). Is this still considered a 100% installation where I can fully utilize a continuous load of 760A? Or must I treat this like an 80% breaker (because of the trip dial change) and only utilize a continuous load of 0.8 x 760A = 608A?