Can anyone explain what "load diversity" is as referenced in appendix B, Table B-310-11.
I would like to put 22(current carrying) - #12 THHN CU wires in a 1" conduit and install on 20 A breakers. These circuits all have minimal loads and are not loaded to their maximum load(no diversity) as referenced in Table 310-15(B)(2)(A). Average load is approx. 6 A.
I am being told that I must derate to 45%.
I feel that I can derate to 70% of my allowable ampacity according to Appendix B, Table B-310-11.
Am I not understanding what is meant by load diversity vs no diversity?
I would be grateful for any input.