Am I getting this right... say I have 6, 8awg thhn ccc in 11/4 emt, table 310.16 in thhn column 8awg has ampacity 55 amps so I figure at table 310.15(B)(2)(a) 4-6 ccc , 80% the 8awg is now only good to 44 amps? What about 14 awg,12 awg,10 awg thhn per 240.4(D) do adjust from 15 a,20a,30a or use the ampacity values from 310.16 to make adjustment factors from above 3 ccc