I do own a scope and am with Al here it is hard to distinguish the type of wave forms..I also have a meggar and you have to be careful not to meggar someones electronics and you might think you have all the outlets covered and do not..the meggar can have a negative effect on a circuit..
I guess we need to look at all aspects but if you pigtail everything on the circuit and make the circuit clean and with no apparent defects. You connect the AFCI it holds for 60 days and you now have a problem..You go and check it out nothing new has been done (electrically or mechanically) and you looked it all over and it takes 2 new arc faults in and out to get one to hold..is it the manufactures fault with faulty equipment or is it the installers fault or the homeowners fault..the installer and home owner suffer the negative effects not the manufacturer..
Now in the above mentioned situation what actually turned out to be the problem was when the wires were pigtail the installer pushed wires into the boxes with his hammer handle and that cause the wires to have a tight bend in the wire and couple with nine splices I figure the wave form was distorted enough to send a false signal back to the breaker. we cut the bends out and shortened the pig tails so the wire had no tight bends in them and circuit has worked fine since then..
Now when we talk about tight bends I mean when the insulation was striped the wire showed stress cracks in it and was discolored..I do not mean severally discolor just the discoloring that comes from stressing copper..It is solid copper we are dealing with here. I did not take pictures sorry..I do wish I would of documented the whole thing now with photos and the like..So has anyone else run into s similar situation..I think I might try and work out a deal with the electrical department at the college.. maybe we can set up a similar situation and see if I can run the tests to verify that this is actually the culprit or if it is just coincedence..But economy is tight and funds tight as well so it is low priority to the budget..
I guess we need to look at all aspects but if you pigtail everything on the circuit and make the circuit clean and with no apparent defects. You connect the AFCI it holds for 60 days and you now have a problem..You go and check it out nothing new has been done (electrically or mechanically) and you looked it all over and it takes 2 new arc faults in and out to get one to hold..is it the manufactures fault with faulty equipment or is it the installers fault or the homeowners fault..the installer and home owner suffer the negative effects not the manufacturer..
Now in the above mentioned situation what actually turned out to be the problem was when the wires were pigtail the installer pushed wires into the boxes with his hammer handle and that cause the wires to have a tight bend in the wire and couple with nine splices I figure the wave form was distorted enough to send a false signal back to the breaker. we cut the bends out and shortened the pig tails so the wire had no tight bends in them and circuit has worked fine since then..
Now when we talk about tight bends I mean when the insulation was striped the wire showed stress cracks in it and was discolored..I do not mean severally discolor just the discoloring that comes from stressing copper..It is solid copper we are dealing with here. I did not take pictures sorry..I do wish I would of documented the whole thing now with photos and the like..So has anyone else run into s similar situation..I think I might try and work out a deal with the electrical department at the college.. maybe we can set up a similar situation and see if I can run the tests to verify that this is actually the culprit or if it is just coincedence..But economy is tight and funds tight as well so it is low priority to the budget..