AFCI and flourescent fixtures

Status
Not open for further replies.

TrevorZ

New member
How do you recommend to install these so that they work together? On suggestion was to install the fixture on a different circuit. Does anyone know of a way that keeps the installation within the NEC limits?
 
Re: AFCI and flourescent fixtures

Not unless you can install the luminaires so they are not fed from an outlet. My understanding is a small amount of leakage is allowed in the product standard for floresent fixtures. How many fixtures are there and what type? If its just one or two I would try a different fixture.
However, an AFCI has a built in GFPE function, if you have a neutral to ground connection in a box, this may be your problem. It may not be the luminaires.
 
Re: AFCI and flourescent fixtures

Originally posted by tom baker:
[QB] Not unless you can install the luminaires so they are not fed from an outlet.
What cycle are you quoting ? 02 changed the receptacle outlet to outlet and this includes all lighting and smoke detectors.
 
Re: AFCI and flourescent fixtures

Originally posted by TrevorZ:
How do you recommend to install these so that they work together? On suggestion was to install the fixture on a different circuit.
See 210.12. If you put the light on a different circuit, that other circuit would suddenly need to be AFCI protected. :)
 
Re: AFCI and flourescent fixtures

We install 1000`s of flourescents a year and AFCI`S tripping has not been a problem unless the breaker trips due to a line to ground/neutral fault.Now the senario of a ground to neutral fault lets say in a receptacle with nothing plugged in the receptacles, will trip when you turn a light on that circuit on ;)
I`m curious what brand of flourescents are you using that cause this :confused:
 