I went to a customers house yesterday to add on a 10 circuit generator panel, no ATS or anything fancy, basic line/off/gen switch. Anyhow he wanted his master bed on one cir, and it was a seimens AFCI. I have never done TS with AFCI's and warned him that it may not work.
It worked on line power fine, as soon as it was kicked to gen, the afci tripped. Of course. I would love to know how the MFG approaches this issue, other than the obvious "cant do that circuit" which as we all know is not really an option with some ppl. Anyone have any experiance with this?