*Note: If Ground Fault Circuit Interrupters (GFCI), Arc Fault Circuit Interrupters (AFCI), or Surge Protector Circuit Breakers were used as the branch circuit protector in the main load center, they MUST be used in the transfer switch. GFCI and AFCI breakers must be installed on the left side of the bus, and an isolated neutral must be connected from the
load to the GFCI or AFCI.
This means that the load neutral needs to be connected with a wire nut to a 3-6 foot piece of white neutral wire, run through the conduit to the transfer switch and connected to the "load neutral" lug on the GFCI or ACFI breaker. Because GFCI and AFCI circuit breakers typically take up more than one space, the overall maximum number of circuits may be reduced from the number shown. Contact Gen/Tran for more information on these circuit breaker types.