AFCI and Multi Wire branch circuit

Status
Not open for further replies.

Greg1707

Senior Member
Location
Alexandria, VA
Occupation
Business owner Electrical contractor
Are AFCI breakers available for a multi wire circuit? I am running 14/3 to an attic addition. Will this work?
 
But some makes of AFCI now omit any ground fault detection, and for those brands two single pole AFCIs with a handle tie can be used for MWBCs.

Cheers, Wayne
 
Yes, unless you need GFCI as well, two-single pole AFCI breakers with a handle tie may work.

But if you want to be safe I recommed running two 14/2 instead.

(Typing at the same time as Wayne.)
 
What about the newer cable that has the extra conductor (white) in the NM cable?
 
But some makes of AFCI now omit any ground fault detection, and for those brands two single pole AFCIs with a handle tie can be used for MWBCs.

Cheers, Wayne
Just asking.
Am I understanding you correctly. You have tied a multi wire branch circuit on two individual AFCI circuit breaker?
I have never tried that.
What's your success rate on nuisance trips?
 
We stopped using /3 wire home runs after AFCI requirements came into existence. Even though they were initially for bedrooms the writing was on the wall they would get expanded. Switched to using /2/2.

I just checked my pricing for "today" 14/2/2 is $.02 more per foot than 2 X 14/2. I will gladly pay the additional $.02/ft to only need 1 cable.
 
Am I understanding you correctly. You have tied a multi wire branch circuit on two individual AFCI circuit breaker?
I have never tried that.
Not personally, but I have been following what various manufacturers specify. Some of then have eliminated any L-N differential current monitoring from their single pole AFCIs. And those manufacturers specify it's OK to supply to a MWBC from two individual single pole AFCIs.

I think the list of manufacturers is GE, Siemens, and maybe Eaton BR. But don't take my word for it, check the manufacturer's literature.

Cheers, Wayne
 
So... interesting...
I personally just hate MWBC, really, even before AFCI, but I get the cost saving, & box fill.
I am surprised that 14/2/2 is just a pinch more than (2) 14/2. That is good. Nice.
 
We stopped using /3 wire home runs after AFCI requirements came into existence. Even though they were initially for bedrooms the writing was on the wall they would get expanded. Switched to using /2/2.

I just checked my pricing for "today" 14/2/2 is $.02 more per foot than 2 X 14/2. I will gladly pay the additional $.02/ft to only need 1 cable.
There is two factors at play. One is price, but you pointed out labor savings , and I agree. But the other thing about the game is box fill issues possible , although that too can be overcome with planning it out where the split up will occur.
 
Some of then have eliminated any L-N differential current monitoring from their single pole AFCIs. And those manufacturers specify it's OK to supply to a MWBC from two individual single pole AFCIs.

I think the list of manufacturers is GE, Siemens, and maybe Eaton BR. But don't take my word for it, check the manufacturer's literature.

In a previous comment in another thread I gave the link to the GE literature that says you can do this. Here it is again: DET-719.

I have now been searching for literature from Siemens confirming you can use their single-pole AFCIs on MWBCs, and have not been able to find any. But it seems obvious, yes? They don't even have a terminal for the neutral circuit wire.
 