So we just failed an inspection because of an inspector's interpretation of NEC705.12(D)(6) "Wire Harness and Exposed Cable arc-Fault Protection- A utility interactive inverter(s) that has a wire harness or cable output circuit rated 240V, 30 Amperes, or less, that is not installed within an enclosed raceway, shall be provided with listed ac AFCI protection."
It is an ACPV system. We used MC cable from the j-box on the roof to the tie-in in the main service panel which was up to spec and he had no problem with that portion.
He called us out for the WIRE COMING OUT OF THE MICROINVERTER TO THE J-BOX. Has anyone else ran into this? Is there a caveat because this portion of the circuit is on the roof and NOT running through the building?
There doesn't seem to be a way to enclose this portion of the circuit in conduit because it would require modifying the cable and housing of the micro-inverter itself which would void the manufacturer's warranty.
Simply installing an AFCI breaker is not an option as Siemens/Murray is the only manufacturer that makes a backfeed-rated breaker and it is pretty pricy and this is not a Siemens panel.
Need help as a huge portion of our jobs are AC modules these days and this kind of crazy enforcement will bring us to a standstill!
Thanks.
It is an ACPV system. We used MC cable from the j-box on the roof to the tie-in in the main service panel which was up to spec and he had no problem with that portion.
He called us out for the WIRE COMING OUT OF THE MICROINVERTER TO THE J-BOX. Has anyone else ran into this? Is there a caveat because this portion of the circuit is on the roof and NOT running through the building?
There doesn't seem to be a way to enclose this portion of the circuit in conduit because it would require modifying the cable and housing of the micro-inverter itself which would void the manufacturer's warranty.
Simply installing an AFCI breaker is not an option as Siemens/Murray is the only manufacturer that makes a backfeed-rated breaker and it is pretty pricy and this is not a Siemens panel.
Need help as a huge portion of our jobs are AC modules these days and this kind of crazy enforcement will bring us to a standstill!