How old is that information? GE no longer has a GFP circuit in their AFCIs and item 2 suggests that GFP sometimes clears the series arc.
2 1/2 yrs old
~RJ~
How old is that information? GE no longer has a GFP circuit in their AFCIs and item 2 suggests that GFP sometimes clears the series arc.
I believe that is about the time frame where GE removed the GFP from their AFCIs.2 1/2 yrs old
~RJ~
This is why you mark up materials. If this is not enough you then need to figure a bit more for installation of afci. I have so few problems with them I don't figure any more than I usually do.
These same arguments were around when gfci breakers & receptacles came on the market
Yeh, I did get over the gfi arguments years ago. And they have come a long way but I never spent several trips and hours on a gfi problem that I couldn't fix versus afci which I have. To find out eventually that when someone's TV would go to a full bright white screen during a program would trip the D..N thing because it didn't like the PWM power supply in it ramping up frequency/pulse width to drive the power requirements to illuminate a bright white screen.
Found this out using my intelliarc meter from Siemens and camp out time with homeowner.
I normally don't have many issues with them either but when I do what a PITA.
Like a customers brand new vacuum (with dual motors), Sometimes blown bulbs (when filament arcs within bulb during its demise), selecting speeds with paddle fan wall controls,
treadmill, LED lighting within refrigerator, just to name a few incidents that were truly nuisance trips which cost me time and money.
I don't wish any of this on you but your day will come as long as you have satisfied customers that repeat call you when an issue arises.
Yeh, I did get over the gfi arguments years ago. And they have come a long way but I never spent several trips and hours on a gfi problem that I couldn't fix versus afci which I have. To find out eventually that when someone's TV would go to a full bright white screen during a program would trip the D..N thing because it didn't like the PWM power supply in it ramping up frequency/pulse width to drive the power requirements to illuminate a bright white screen.
Found this out using my intelliarc meter from Siemens and camp out time with homeowner.
I normally don't have many issues with them either but when I do what a PITA.
Like a customers brand new vacuum (with dual motors), Sometimes blown bulbs (when filament arcs within bulb during its demise), selecting speeds with paddle fan wall controls,
treadmill, LED lighting within refrigerator, just to name a few incidents that were truly nuisance trips which cost me time and money.
I don't wish any of this on you but your day will come as long as you have satisfied customers that repeat call you when an issue arises.
That stuff is beyond crazy. I don't think I'd have the patience or figure-it-outiveness to get to the bottom of those problems.
Not an outright Mae Culpa but I talked to a GE dude who told me how they did not have so many electronic loads to be aware of when they made the breakers I had installed that were nuisance tripping when the home owners tried to watch tv or use their Dyson vacuum.Has any one at SQ D, Cutler Hammer, GE, Siemens acknowledged the problems noted in mopowr's post
Has any one at SQ D, Cutler Hammer, GE, Siemens acknowledged the problems noted in mopowr's post
AFCI – Arc Fault
Your treadmill runs on an electric motor. These motors as part of normal use may arc within the motor. This may cause the Arc Fault breaker to trip.
I believe that is about the time frame where GE removed the GFP from their AFCIs.
it was demonstrated that a Branch/Feeder AFCI
incorporating equipment ground fault protection (30 mA trip) is capable of
terminating a glowing connection and the associated heating effects by sensing
the differential current associated with thermal degradation of the wiring device
insulating material(s
Methinks it rather obvious i could, given enough $$$, have my dog listed for fluent Latin
he could (for a biscuit or two) then make a presentation to the CMP
the NEMA task force providing translations .....
~RJ~
Which begs the Q, where are our branch ciruit afci's ?
If in fact we could purchase them , i'm fairly sure the old split buss panels would gain popularity again
~RJ~
(3) A listed supplemental arc protection circuit breaker installed
at the origin of the branch circuit in combination
with a listed outlet branch-circuit type arc-fault circuit
interrupter installed at the first outlet box on the branch
circuit where all of the following conditions are met:
a. The branch-circuit wiring shall be continuous from
the branch-circuit overcurrent device to the outlet
branch-circuit arc-fault circuit interrupter.
b. The maximum length of the branch-circuit wiring
from the branch-circuit overcurrent device to the
first outlet shall not exceed 15.2 m (50 ft) for a
14 AWG conductor or 21.3 m (70 ft) for a 12 AWG
conductor.
c. The first outlet box in the branch circuit shall be
marked to indicate that it is the first outlet of the
circuit.
Obviously a Siemens employee who was a member of MH's forum.Quite a few years ago Bryan (bphgravity) posted something from Siemens acknowledging issues with vacuums and other equipment.