charlie b said:The language says that all circuits that supply outlets in bedrooms shall have AFCI protection. That is in NEC article 210.12. The definition of "outlet," in NEC article 100, tells us it is a place where current is taken from the premises wiring system to supply utiliztion equipment. This would include receptacle outlets, lighting outlets, smoke detector outlets, and some others. The inspector is correct.
resistance said:I believe the inspector is enforcing the 2008, based on what the OP said.
resistance said:I believe the inspector is enforcing the 2008, based on what the OP said.
I don't think so. We all know that even the 2005 required circuits that serve bedroom lighting outlets to be protected by AFCI. We also know that what the 2008 version did was to extend this requirement beyond the bedrooms. But the original question might have been intended two ways.480sparky said:Or the '05 with local amendments.
This part is pretty lucid.It was my understanding the AFCI's are required specifically in Bedrooms.
Here is where the 2008 comes into play. It sounds like the OP installed AFCI's for the bedrooms only, and now gets a ruling that the 2008 requires more.My inspector (Park City, Utah) is requiring all receptacle AND lighting circuits to be on them as well.
Then the inspector is wrong!G0049 said:I think Charlie's right. According to Park City's website, they're on the 05 code with no local amendments.
The inspector is wrong, if he or she is requiring outlets outside the bedroom to be AFCI protected. Read what the OP said:If your permit was pulled before the 2008 was adopted then go for Charlies Definition- aka- the inspector is right.