A discussion an another thread prompted some research on my part. A telephone call to our Bureau of Construction Codes revealed the following:
On Feb 8th, 2016, arc-fault circuit interruption devices will NOT be required on ANY circuit in 1- and 2-family dwellings and townhouses not more than 3 stories above grade plane in heightwith a separate means of egress and their accessory structures. per the Michigan Residential Code, Chapter 8.
http://www.michigan.gov/documents/lara/lara_bcc_2015_residential_code_502813_7.pdf
Arc-fault protection will be required as per the NEC's specs on other structures as covered by the Michigan Electrical Code.
But, hold on to your hat, the relief for 1 & 2 family dwellings, etc., is now under fire with HB 5123.
HOUSE BILL No. 5123
December 8, 2015, Introduced by Reps. Geiss, Goike, Cochran, Yanez, Hovey-Wright, Howrylak and Price and referred to the Committee on Regulatory Reform.
http://www.legislature.mi.gov/(S(l4...ge=getobject&objectname=2015-HB-5123&query=on
So far, all that has happened was that the bill was read and has now been referred to the Committee on Regulatory Reform.
However, even AFTER Feb 8th, if HB 5123 makes it into law, it will trump the MRC exemption.
This will be interesting to follow, as I would hazard that none of the politicians voting know anything at all about AFCIs or anything electrical for that matter.
The proposed bill states that ALL BRANCH CIRCUITS will require AFCI's, no exceptions.
This will be interesting to watch.
On Feb 8th, 2016, arc-fault circuit interruption devices will NOT be required on ANY circuit in 1- and 2-family dwellings and townhouses not more than 3 stories above grade plane in heightwith a separate means of egress and their accessory structures. per the Michigan Residential Code, Chapter 8.
http://www.michigan.gov/documents/lara/lara_bcc_2015_residential_code_502813_7.pdf
Arc-fault protection will be required as per the NEC's specs on other structures as covered by the Michigan Electrical Code.
But, hold on to your hat, the relief for 1 & 2 family dwellings, etc., is now under fire with HB 5123.
HOUSE BILL No. 5123
December 8, 2015, Introduced by Reps. Geiss, Goike, Cochran, Yanez, Hovey-Wright, Howrylak and Price and referred to the Committee on Regulatory Reform.
A bill to amend 1972 PA 230, entitled
"Stille-DeRossett-Hale single state construction code act,"
(MCL 125.1501 to 125.1531) by adding section 4a.
THE PEOPLE OF THE STATE OF MICHIGAN ENACT:
SEC. 4A. (1) ALL BRANCH CIRCUITS THAT SUPPLY 120-VOLT, SINGLE-
PHASE, 15- AND 20-AMPERE OUTLETS SHALL BE PROTECTED BY A
COMBINATION TYPE OR BRANCH/FEEDER TYPE ARC-FAULT CIRCUIT
INTERRUPTER INSTALLED TO PROVIDE PROTECTION OF THE ENTIRE BRANCH
CIRCUIT. HOWEVER, THE LOCATION OF THE ARC-FAULT CIRCUIT INTERRUPTER
SHALL BE PERMITTED TO BE AT OTHER THAN THE ORIGINATION OF THE
BRANCH CIRCUIT IF BOTH OF THE FOLLOWING APPLY:
(A) THE ARC-FAULT CIRCUIT INTERRUPTER IS INSTALLED WITHIN 6
FEET (1.8 M) OF THE BRANCH CIRCUIT OVERCURRENT DEVICE AS MEASURED
ALONG THE BRANCH CIRCUIT CONDUCTORS.
(B) THE CIRCUIT CONDUCTORS BETWEEN THE BRANCH CIRCUIT
OVERCURRENT DEVICE AND THE ARC-FAULT CIRCUIT INTERRUPTER ARE
INSTALLED IN A METAL RACEWAY OR A CABLE WITH A METALLIC SHEATH.
(2) SUBSECTION (1) IS ADOPTED AS MODIFICATION OF THE RELEVANT
PROVISIONS OF THE INTERNATIONAL RESIDENTIAL CODE.
http://www.legislature.mi.gov/(S(l4...ge=getobject&objectname=2015-HB-5123&query=on
So far, all that has happened was that the bill was read and has now been referred to the Committee on Regulatory Reform.
However, even AFTER Feb 8th, if HB 5123 makes it into law, it will trump the MRC exemption.
This will be interesting to follow, as I would hazard that none of the politicians voting know anything at all about AFCIs or anything electrical for that matter.
The proposed bill states that ALL BRANCH CIRCUITS will require AFCI's, no exceptions.
This will be interesting to watch.