If I have a fan coil unit in the ceiling of a bedroom on a dedicated 15A circuit, is AFCI protection required?
IMO yes.If I have a fan coil unit in the ceiling of a bedroom on a dedicated 15A circuit, is AFCI protection required?
Perhaps worded slightly better: Is the "outlet" for the fan coil unit accessed from the bedroom? If not, then where is it accessed from?Is the "outlet" for the fan coil unit in the bedroom?
Bathroom???The code wording is poor. It does not say how is the outlet accessed. It says all in the bathroom need a AFCI protection. In my opinion this outlet is not in the bedroom. I am sure that the intent is for this circuit to have AFCI protection, but that is not what the words say.
Still yes IMO.Recessed into the ceiling, accessed through the integral door of the FCU flush in the ceiling.
The receptacle outlets are accessed from the room as is a surface mounted light fixture. It appears to me that the outlets for this fan coil unit or for a recessed light fixture are not in the room and not subject to the AFCI rule as it is written. I agree with you that would be the intent, but you can only enforce the written rule, not the intent.Bathroom???
I know it does not say accessed. It was an attempt towards intent. Say you have a kitchen next to a bedroom. All the outlets of issue are in the dividing wall. None are actually in the kitchen or the bedroom. The outlets are in the wall. The distinguishing difference in the application of the arc-fault requirement is enforced by which side the outlet is accessed from.
I tried talking to my phone instead of typing and did not pay close enough attention to what it though I said.Bathroom??? ...
I'm willing to bet a substantial portion of AHJ inspectors will not agree with you on that remark.... you can only enforce the written rule, not the intent.
The receptacle outlets are accessed from the room as is a surface mounted light fixture. It appears to me that the outlets for this fan coil unit or for a recessed light fixture are not in the room and not subject to the AFCI rule as it is written. I agree with you that would be the intent, but you can only enforce the written rule, not the intent.
Since I am not a fan of the AFCI and don't believe that they really provide any meaningful protection, I would like to say that the box setback would negate the rule but I won't go that far. For you application, I don't think the code wording requires AFCI protection. Like I said before I am sure that the intent is that AFCI protection be providrd for that circuit, but the code wording does not support that.Don, the receptacle outlets would be recessed into the wall up to .25". The lighting outlet bearing the surface luminaire is as well. Do you believe box setback negates AFCI protection?
IMO yes.
I would say yes.
Chris
I would have to go with Don on this. The outlet is not in the bedroom.
I see the recessed can as being accessible from the bedroom as the socket is available from the room thus afci is required. The socket is the true outlet the JB is just a connection.