I would have to go with Don on this. The outlet is not in the bedroom.
I see the recessed can as being accessible from the bedroom as the socket is available from the room thus afci is required. The socket is the true outlet the JB is just a connection.
Dennis, I am confused-you say you agree with Don and then say AFCI protection is required..I thought Don was saying the opposite.:?