1) Hal is asking if AFCI tripped with plain old 3-prong receptacle instead of a GFCI.
Actually I didn't but that is a good question. I assumed it did.
-Hal
1) Hal is asking if AFCI tripped with plain old 3-prong receptacle instead of a GFCI.
Most AFCI's that I install are for existing wiring, new outlets, & old work. My clients are educated why its in there best interest that no legal cause exists for property insurance to void claims, including checking the smokes & batteries.
Many remodel contractors on this forum openly refuse to install AFCI's, subjecting their clients to denial of claims by insurance investigators.
Granted owner-builder remodels are rarely inspected, and its not enforced, but I believe refusing required Smokes or AFCI's is negligent disregard for duty of care, and fails to protect owner builders from themselves.
DON'T lump AFCIs together with smokes! Smoke and CO detectors along with sprinklers are proven lifesavers. Fire marshals, fire inspectors and building inspectors will issue a violation if they find that there are no smokes or that they are inoperative and not maintained.
In the absence of a permit and an original electrical inspection there is nobody that goes around looking for AFCIs. I have never heard of an insurance company denying a claim because there were no AFCIs installed. Trying to prove that an AFCI would have saved a life would be like trying to prove that Bigfoot exists and they know it.
Maybe in the Peoples Republic of California but nowhere else.:happyyes:
-Hal
1) Hal is asking if AFCI tripped with plain old 3-prong receptacle instead of a GFCI.
Actually I didn't but that is a good question. I assumed it did.
-Hal
A major legal battle over it would create the litmus test that finally puts this debacle to rest.
-Hal
The Risks are Real!
Arc-faults are the cause of a significant number of electrical fires in homes. In fact, an estimated 1,500 fires caused by electrical loss(1) were reported in Ontario over the past five years, resulting in an average of six fatalities per year
(1) involved some type of electrical failure or malfunction as a factor contributing to ignition.
DON'T lump AFCIs together with smokes!
Maybe in the Peoples Republic of California but nowhere else.:happyyes: -Hal
So is your problem the AFCI trips when said GFCI is in the circuit but doesn't trip with same load and no GFCI? Sorry, but this is first post that gave me that idea, even though it may be what you have been trying to get at from the beginning.I went back and did the test.
Hair dryer plugged directly into plain old 3 prong. No trip.
Now I plug the dryer into the old GFCI, and old GFCI into the plain old 3 prong. It worked for 20 seconds, then I gave the GFCI a slight shake and it tripped. Next trial no shake required, it tripped right away.
Contractors that complete projects with extension-cord wiring, missing Smokes, or improper fuses, usually can’t figure out AFCI’s among other things, and refuse to acknowledge any violation, much less how it becomes apparent to claims adjustors... With no licensing standard between States, no electrical certification required for any general contractor, laborer, or owner builder doing electrical, and licensing regulators stripped of enforcement budgets, the competitive bid process that demands skills for GFCI, and AFCI devices, is perhaps the only reliable screen against incompetent contractors ...
One of my pensioner clients was cancelled by phone, over a water damage claim, and no other insurance carrier would sell a new policy. They had to move into an association-insured condo. ...Other clients employed with insurance carriers are familiar with scripted procedures, and Artificial Intelligence systems, used to screen claims for cause. ...No Fire Marshal or inspector report was needed to deny the claim by phone, and challenging bad-faith insurance involves costly litigation, or settlement out of court.
So is your problem the AFCI trips when said GFCI is in the circuit but doesn't trip with same load and no GFCI? Sorry, but this is first post that gave me that idea, even though it may be what you have been trying to get at from the beginning.
Unless a replacement does same thing, just consider it defective or that something has failed. Send it in if you want to I guess.Yes that's correct.
And what I was trying to say from the start.
I now have the bad GFCI jacked into a old appliance cord, and can move it from outlet to outlet.
All it takes is a small mechanical shake of the GFCI to trip the AFCI. I suspect that the laundry machine was supplying that shake, in the original failure case.
I'm considering sending the GFCI to Leviton for analysis, if anyone at Leviton caress.
..In most coastal areas here there are properties that are basically uninsurable. If a storm damages them they can't be rebuilt..
After paying premiums for 20 years over 350,000 homeowner policies are being dropped In and around Paradise California. No refund of premiums.
https://www.eastbaytimes.com/2019/0...p-insurance-companies-drop-long-time-clients/
Once I narrowed it to the GFCI, I pulled it, and used an old appliance cord to make a little
ever-so-safe test rig:
Yes. Minor plumbing leak from upstairs bath, which damaged down stairs drywall over time...As to your customer, most homeowner policies (at least here) exclude water damage unless maybe from a leaky roof. Then there are storm and flood exclusions. ..My take is that the damage wasn't covered..
Agree, property owners need better protection than detrimental reliance on property insurance...Absent a mortgage, you don't need insurance and there are many people who are comfortable without it. They probably figure what are the odds of a total loss in their case and putting money aside every month to cover any damages is better than giving it to some insurance company who won't pay out.
Shaking of the old GFCI trips the AFCI.
You can hear it rattle when shook.
A new GFCI solved the problem, but AFCIs are to blame? :blink: