- Chapel Hill, NC
- Retired Electrical Contractor
Don, this is the section that was quoted. He said he was at the big meeting in California and the cmp stated this will be passed. So how do you read this...
Draft 2104 210.12(A) said:(2) A listed outlet branch circuit type arc-fault circuit interrupter installed at the first outlet on the branch circuit where all of the following conditions are met:
a. The branch circuit over current protection device shall be a listed circuit breaker having an instantaneous trip not exceeding 300 amperes.
b. The branch circuit wiring shall be continuous from the branch circuit overcurrent device to the outlet branch circuit arc-fault circuit interrupter.
c. The maximum length of the branch circuit wiring from the branch circuit overcurrent device to the first outlet shall not exceed 15.2 m (50 ft) for a 14 AWG or 21.3 m (70 ft) for a 12 AWG conductor.
d. The first outlet box in the branch circuit shall be identified.