Fordy said:
What if an apartment you want to add 120 volt smoke alarms to has a Federal Pacific Stablok Panel and Arc Fault Breakers are not available for it.
Well, Fordy, I'd say, given ELI's clear statements on the matter, the only relief the owner of the apartment building will get will come from a conversation with the inspectors that will inspect the building.
Being clear about the local smoke detector ordinance will be necessary. The number of units in the apartment building may also be important, depending upon whether local, or State, smoke detector ordinance is in play.
That is, does the smoke really have to be line powered?
The FPE problem, as noted above, is handled by installing a subpanel. If the existing branch circuit is in good enough shape to reside peacefully on an AFCI, then one can simply reconnect on the AFCI. . . .That simplistic idea assumes
a lot! The existing circuit can't be a multiwire (at least not yet, until two pole combo AFCIs are sold) and the entire circuit has to be in good condition without neutral - EGC connections. Also, any of the existing splices must be solid, and the receptacle contacts and switch mechanisms need to work reliably with minimal, or no, arcing. If you can vouch for this, or want to gamble that the existing branch circuit is this good, then, re-connect it to the AFCI.
Otherwise, run a new homerun.