czars
Czars
- West Melbourne, FL
- Florida Certified Electrical Contractor
The 2011 NEC will be in effect in Florida on June 30, 2015. I do a lot of repair work for older folks who live in manufactured homes and receptacle replacement is common.
The 2011 NEC, Article 550.13(A)(2) specifically requires that receptacles in manufactured homes be installed IAW Article 406.4. 406.4 requires that when receptacles are replaced where AFCI protection is required by the 2011 NEC, AFCI protection must be provided by AFCI breakers or receptacles. However, 406.4 does not refer to Article 210.12(A) which requires a metal raceway or cable between the standard breaker and an AFCI receptacle at the beginning of the circuit.
Many of the manufactured homes have Westinghouse, Challenger or Bryant service panels for which AFCI breakers are not available. Thus, to provide AFCI protection, I would have to use AFCI receptacles. My question is: To utilize AFCI receptacles, would I have to install a metal raceway or cable between the service panel, using a standard breaker, and the AFCI receptacle as the first receptacle in the circuit?
