Afci keeps tripping help!

Status
Not open for further replies.
Since any load applied trips the breaker, my money is on the wrong neutral is terminated on the AFCI breaker, it's easy to do in a resi panel because the cables are usually so close together, with multiple cables in the same clamp ect. Double check that it is comming from the same cable, and I think you will find your problem. :)
 
Actualy the breaker resets and holds until a load is applied.:)

That is almost always an indication of a parallel path for neutral current, assuming the load is not causing an arc.

Exactly. Thank you Don.

I'm predicting a box with power from two circuits and a bad neutral make up, once discovered and corrected, will solve the problem.
 
Yes about the wrong neutral , believe me I double checked because before I started wiring the new panel I put black 33 around the black and white of each circuit and it's very easy to follow the neutral back to the connectoor ,but it is something to add to a trouble shooting list thanks . One other thing I failed to mention and it might or might not matter but I noticed that the doorbell transformer is tied to this circuit , would that have any affect ? And yes I'm thinking it might be the fan it is a bit noisy ! I'm going to check all. This Wednesday.
 
And yes I'm thinking it might be the fan it is a bit noisy ! I'm going to check all. This Wednesday.
As mentioned earlier - variable speed motors and AFCI's are not exactly the best of friends... They often create simular waveform distortion as the pre-programed 'arc signatures' these devices seek.
 
YES it doesnt trip any more finally ohhh man that was reallly bugging me . thank you everybody for your input and man these afci can really be a pain in the you know where . I did exactly what ya told me i removed the neutral from that crcuit and ohmed it out to the neutral bus and took off one nuetral at a time and then realized alll the neutrals were off and i stilll had contnuity , so then i removed the bonding screw and still themn i removed the grounds and still so after that i was left with the branch circuit graonds and the nuetral . so we narrowed it down to a nuetral touching ground sure enough in the last receptacle in the circuit the ground was barely touching just enough to trip the afci . man these breakers can be a pain THANKS everybody for your input .
 