shockin said:
I'm not sure how an AFCI functions or if that would affect it, and why it doesn't affect the other two. . .
An AFCI has several features. With respect to your problem, here is a list of the ones that relate, in my opinion.
Part of the circuitry behaves like a GFI with a trip of around 50 milliamps (not 5.0 as in a standard GFCI). To turn on and stay on, the AFCI circuitry has to see a load side neutral that has no contact with the EGC. Any accidental contact will trip the breaker.
Another part of the AFCI circuitry is a signal processor that is only turned on when it sees a signal that exceeds 50 to 70 amps. For the Branch / Feeder AFCI (that you would have installed in this Master Bed circuit a year ago) the signal processor then determines if the waveform is a good or bad arc. If the circuitry sees this "bad" high current spike in a half cycle, and then sees another within eight half cycles, the signal processor tells the breaker to trip.
Lightning creates an electromagnetic pulse (EMP) that can induce significant currents and voltages in conductors, even at a distance. It's easy to suspect this, but it will be extremely difficult to document.
This gets to the real issue surrounding AFCI troubleshooting, in my opinion. An AFCI has a number of things that cause it to trip, but, aside from the trip itself, the AFCI keeps secret what AFCI function actually initiated the trip.
As a result of this secrecy, the troubleshooting electrician must eliminate trip causes by showing what
couldn't have caused the trip. One has to show that the branch circuit is, in fact, free of defects. Eliminating the branch circuit allows pointing a finger at the utilization equipment connected to the branch circuit at the outlets (lighting or receptacle or smokes), OR, at the breaker itself.
The first, least time involvement, method will be to replace the AFCI with another, of known condition, and wait.