Thanks for the responses so far. Here's an update:
The electricians were out last wednesday and I had them take the tankless (gas) water heater off one of the branch circuits and put it on it's own dedicated non-AFCI circuit and they installed a whole house surge protector on the panel in an attempt to eliminate potential noise. The tripped AFCI breakers escalated immensely. They had 2-6 breakers tripping at a time. Yesterday, the homeowner claimed it happened 18 times for a total of 44 tripped breakers. They mentioned off-hand that it happens frequently when they use the hot water. The new circuit for the water heater was at the top of the panel so the electrician moved it to the bottom of the panel and voila! Only one breaker is tripping and seemingly only when the hot water is engaged. Time will tell if this was in fact the issue. This makes no sense to me because everything is connected on the buss and it shouldn't matter where it is on the panel, correct? I can understand problems happening on one leg or phase over the other, but why would it matter where it was attached on the bus? Could be the inductive carryover mentioned by someone else above?
Also, the CH rep claims one breaker can't trip the others. Makes sense to me but it's what seems to be happening. The electrician was on the phone to the water heater engineers and traced it down to a malfunctioning component on the water heater that will be sent to us and installed friday, I hope. Also, the CH rep is sending all new breakers that have some kind of filter or surge protection built in to make them a little less sensitive to whatever is going on in the panel. If this works, I'll post the results and hopefully save someone else a lot of trouble who reads this.
We've ordered the diagnostic tool from Siemens and it should be in tomorrow. I suspect it would have helped us pinoint the water heater as the problem. If so, it would have saved us a lot of money and grief over the $350 price tag for it. We'll go ahead and test everything else with the tool to make sure nothing else is going on. More to come.......
The electricians were out last wednesday and I had them take the tankless (gas) water heater off one of the branch circuits and put it on it's own dedicated non-AFCI circuit and they installed a whole house surge protector on the panel in an attempt to eliminate potential noise. The tripped AFCI breakers escalated immensely. They had 2-6 breakers tripping at a time. Yesterday, the homeowner claimed it happened 18 times for a total of 44 tripped breakers. They mentioned off-hand that it happens frequently when they use the hot water. The new circuit for the water heater was at the top of the panel so the electrician moved it to the bottom of the panel and voila! Only one breaker is tripping and seemingly only when the hot water is engaged. Time will tell if this was in fact the issue. This makes no sense to me because everything is connected on the buss and it shouldn't matter where it is on the panel, correct? I can understand problems happening on one leg or phase over the other, but why would it matter where it was attached on the bus? Could be the inductive carryover mentioned by someone else above?
Also, the CH rep claims one breaker can't trip the others. Makes sense to me but it's what seems to be happening. The electrician was on the phone to the water heater engineers and traced it down to a malfunctioning component on the water heater that will be sent to us and installed friday, I hope. Also, the CH rep is sending all new breakers that have some kind of filter or surge protection built in to make them a little less sensitive to whatever is going on in the panel. If this works, I'll post the results and hopefully save someone else a lot of trouble who reads this.
We've ordered the diagnostic tool from Siemens and it should be in tomorrow. I suspect it would have helped us pinoint the water heater as the problem. If so, it would have saved us a lot of money and grief over the $350 price tag for it. We'll go ahead and test everything else with the tool to make sure nothing else is going on. More to come.......