I have a customer whose home was wired by either an inexpensive (you get what you pay for) or inexperienced electrical contractor or DIY general contractor. Regardless, I continue to find issues with this house after correcting 41 of the 65 inspection violations that the private inspector, hired by the homeowner, came across during his very thorough inspection.
Recently, I was called to handle "lights going out" when they took showers and had the exhaust fan running. I figured it was a GFCI issue and took a look. What I found was that the bath, bedroom and dining room circuits (lighting/fan and power) other than the required 20A receptacle at the basin were all on an arc fault breaker. I've been trying to isolate the source of the possible "nuisance" tripping or other arcing that may be occurring on this circuit.
Question: Are arc fault breakers known for nuisance tripping in cases like this where it's possible moisture in the fan is getting across some terminations in a modular plug, or even the motor, and causing the problem?
Bigger Question: I heard that, but have yet to verify, arc fault breakers are going to be required in bath circuits including fans. I see a potential for nuisance tripping in this case, if it is just a moisture issue.
FYI: this is a very small bathroom and the shower is close to 40% of the space. Lots of condensate and a 110 CFM fan, which I am probably going to replace with a larger capacity unit.
Anyone with similar scenario and advice please comment. I don't want to replace the unit and have the same thing happen again.
Thanks!
Recently, I was called to handle "lights going out" when they took showers and had the exhaust fan running. I figured it was a GFCI issue and took a look. What I found was that the bath, bedroom and dining room circuits (lighting/fan and power) other than the required 20A receptacle at the basin were all on an arc fault breaker. I've been trying to isolate the source of the possible "nuisance" tripping or other arcing that may be occurring on this circuit.
Question: Are arc fault breakers known for nuisance tripping in cases like this where it's possible moisture in the fan is getting across some terminations in a modular plug, or even the motor, and causing the problem?
Bigger Question: I heard that, but have yet to verify, arc fault breakers are going to be required in bath circuits including fans. I see a potential for nuisance tripping in this case, if it is just a moisture issue.
FYI: this is a very small bathroom and the shower is close to 40% of the space. Lots of condensate and a 110 CFM fan, which I am probably going to replace with a larger capacity unit.
Anyone with similar scenario and advice please comment. I don't want to replace the unit and have the same thing happen again.
Thanks!