Hope this is the right place to ask this question. I was working on a residential trim out today and went to power up the circuits and had an AFCI instantly trip. I tore the circuit apart. removed all the switches and receptacles, ohmed everything out and found nothing. Put it all back together again, turned the breaker on and "POP". I finally tracked it back to an exhaust fan/light that is on that breaker. I know the bathroom isnt specifcally required to be on the AFCI, but since the only way into the bath is through the bedroom it was "suggested" that I put the bath lights on the bedrooms AFCI circuit. Now the question,, Has anyone else ran into this type of situation where a small motor as on the exhaust fan causes the AFCI to trip? or am I looking at a breaker problem? The breaker in question is a Seimens 15A AFCI, and the fan is a Broan model 678 fan/light combo. Thanks in advance.