1793 said:The ball game comes on tonight at 10:00. You have til then to get back with us or I won't be able to sleep. :grin:
electricmanscott said:More later but to start, AFCI trouble shooting, called Siemens, response amounted to go poop in a hat, nothing we can do for you.
![]()
Be back with story....
Would you expect P&S to tell someone over the phone how to wire up a set of 3-ways that they had screwed up?electricmanscott said:Of course I say shouldn't YOU as the people who actually made the product be the one to assist with technical questions? "No sir we do not offer technical support for this product." WHAAAATTTT????
electricmanscott said:I have not ruled out a wiring issue yet. It could very well be something I did or whatever with the wiring.
electricmanscott said:Both are loaded with recessed lighting and dimmers. The other AFCI circuits feeding receptacles are fine. Common link?
mdshunk said:Would you expect P&S to tell someone over the phone how to wire up a set of 3-ways that they had screwed up?
.
480sparky said:I understand your frustration, but if you don't know what the cause is, how can a tech trouble-shoot it over the phone? They may provide some suggestions, but that's all you can expect.
mdshunk said:This isnt' really exotic technology. There are two reasons AFCI's trip, and there is test equipment for both. Get some and learn how to use it. Here's my unconditional money back guarantee... with a megger and the requisite training on how to use it, you can find the precise reason why any AFCI is tripping in less than 4 hours (if you're slow).
electricmanscott said:Ok, I'm game. Where do I get this training?
growler said:Those recessed fixtures could be the key to this. This is just a guess but it seems to me that almost anything could cause a series arc. This could be a loose connection ( darn hard to check with a bunch of recessed cans ) or something as simple as a loose lamp that maybe vibrates at times ( people walking on the floor above ).
I think I would check each and every lamp in every fixture to make sure they are seated properly. If that doesn't work I would check the wires to the lamp sockets.
What may have to happen in the future is that recessed cans may need to be burned in for a couple of days before the sheet rock goes up.
This is just an idea. If it sounds crazy feel free to ignore. :smile: