Well, to carry my point to the extreme, . . .
Hypothetical situation: A receptacle outlet could be installed in a bed under the NEC pre-210.12(B) and have never been connected to a "branch circuit" (installer and inspector oversight). Later, say today, under the 2008 NEC, one connects a branch circuit, a branch circuit connected to an OCPD, to that same receptacle outlet. The old receptacle outlet is added to the "branch circuit", now, and, since the complete "branch circuit" to the old receptacle outlet is new, i.e., it had never been installed with the original receptacle outlet, 210.12(B) is invoked. Before there wasn't a complete branch circuit, after, the branch circuit is completed, for the first time, to the old receptacle outlet.
A different hypothetical: A bedroom branch circuit has a homerun to its OCPD. This bedroom is wired to a pre-210.12(B) NEC. The homerun passes through a kitchen on the way. Today, under the 2008 NEC, a kitchen remodel occurs, and the alterations require the electrician to replace 20' of original bedroom branch circuit homerun, and reroute the homerun along a new path 28' long. No new outlets are added on the bedroom branch circuit. 210.12(B) is NOT invoked, in this case, because the "branch circuit" existed before, under a previous Code, and continues to exist. The wiring method(s) installed in the reroute, the new path 28' long, would be installed to the requirements of today's NEC, but 210.12(B) isn't invoked because a new branch circuit is not added.