Re: AFCI testers (Ideal Shure Test)
The first set of breakers was changed out on the first red tag and the second set was from brand new batch that I switched around to see if it made a difference, But no matter what the Ideal Shure Test would not trip them. Putting the receptacle on a shorter wire would allow it to trip. So I know the breaker was doing it's job (as far as UL specs) but I haven't had time to do more research into it to see if other brands are affected?
It is Steve's statement that has me perplexed:
The first set of breakers was changed out on the first red tag and the second set was from brand new batch that I switched around to see if it made a difference, But no matter what the Ideal Shure Test would not trip them. Putting the receptacle on a shorter wire would allow it to trip. So I know the breaker was doing it's job (as far as UL specs) but I haven't had time to do more research into it to see if other brands are affected?
It is Steve's statement that has me perplexed:
It sounds like this problem is already known and was swept under the carpet? Or why has the manufactures been allowed to divert from the original spec's of 75 amp's?Most AFCI's are designed to trip at 75 amps fault current (and most mfrs. put a safety margin in so actual trip levels are at 35 to 60 amps) . It seems that with an indicator producing 75 amps, it would take significant impedance for an AFCI to not trip considering the 35-60A trip points they are designed for.