Would a wall mount forced hot water heating unit with a blower require afci protection?
Kind of a backhander there tom wouldn't you say? Sheesh. I would hope I would know what a branch circuit is at this point. As for an outlet I wouldn't consider this to be one but I thought I'd get some opinions.Review 210.12, and definitions for outlet and branch circuit.
Its as much an outlet as the notorious smoke detectors areOriginally posted by electricmanscott:
Tom it is a dwelling bedroom, it is a 15 amp 125 v circuit, it is fed from a circuit breaker.
Kind of a backhander there tom wouldn't you say? Sheesh. I would hope I would know what a branch circuit is at this point. As for an outlet I wouldn't consider this to be one but I thought I'd get some opinions.Review 210.12, and definitions for outlet and branch circuit.
Originally posted by tonyi:
Its as much an outlet as the notorious smoke detectors are )
Smoke detectors, light fixtures and wall mounted heaters are all utilization equipment.
However the smoke detectors like light fixtures are mounted to an outlet box. The outlet falls under the AFCI requirement.
The wall mounted heater has no outlet box, the wiring method goes directly into the heater, no outlet box no AFCI.
Bob
[ October 28, 2003, 06:09 PM: Message edited by: iwire ]
Article 100Originally posted by iwire:
The wall mounted heater has no outlet box, the wiring method goes directly into the heater, no outlet box no AFCI.
Originally posted by iwire:
That's my story and I am sticking to it.
If we call the point where NM ends an outlet, wouldn't a feed brought to a switch in the bedroom to feed a light elsewhere need to be AFCI?
The outlet definition does not say the final point.
I run a NM from a panel and come up short and I add a J Box and continue on to supply utilization equipment.Outlet. A point on the wiring system at which current is taken to supply utilization equipment.
Is that NM from the panel in the J Box an outlet?
It is a point where current is taken to supply utilization equipment.
IMO The definition should say something like the following.
"The final point on the wiring system at which current is taken to supply utilization equipment."
The way the definition is now I have always taken it to mean that an "outlet" is something the end user deals with, receptacles or light sockets.
If I read it to mean any point that power is taken it gets a little broad.
[ October 29, 2003, 03:57 AM: Message edited by: iwire ]
You are correct that you don't "take" current from the smoke detector, but the smoke detector "takes" current from the building wiring system. The point at which the smoke detector is connected to the building wiring system is the outlet.You cannot take current from a smoke detc.
No, the power is not being directly supplied to the load at that point in the circuit.If we call the point where NM ends an outlet, wouldn't a feed brought to a switch in the bedroom to feed a light elsewhere need to be AFCI?
Now to make the discussion real interesting...Originally posted by don_resqcapt19:
No, the power is not being directly supplied to the load at that point in the circuit.
Don