New AC and furnace professionally installed 4 months ago. Once cold weather hit, the 20A AFCI breaker for the furnace tripped. Wiring to furnace is through metal conduit. Furnace is only device on the circuit. After 1st trip, installer checked wiring connections. After 2nd trip, next day, installer replaced ACFI with 20A GFI breaker. Stated the ACFI was likely reacting to variable speed blower motor looking like an arc fault.
Still also considering possible amp draw issue. Due to filter being directly against the furnace enclosure, I don’t have a handy place to drill to insert a manometer tap to check pressure rise across the blower. The prior unit had a little length of duct after the filter for inlet pressure and also a handy tapping hole near heat exchanger coils for outlet pressure. So I can’t tell yet if it was too much load on the motor. We’ll have a cold spell this weekend, so if it’s motor load, the new 20A GFI only breaker should trip.
I have found a reference, but it’s AI -not real intelligence, that supports the installers claim:
“High Frequency Capacitive Leakage
Many modern furnaces with variable speed blower motors may not be compatible with AFCIs. They can produce high-frequency electrical noise that triggers the breaker.”
If this is the case, I would have expected it to come up elsewhere in the forum unless it is such common knowledge that no one uses AFCI with a furnace. No mention of it in the furnace installation info.
NFPA 70, NEC 2023 article 210.12 seems to indicate AFCI is required: “AFCI protection shall be installed in accordance with 210.12(B) through (E). In 210.12(B) it lists various rooms, closets, hallways and the catch-all “Similar areas”. No mention of what constitutes a “similar area”. It provides exceptions only for fire alarms and arc welders.
The furnace is in an unfinished basement.
So I have 2 concerns. Only the first applies to this forum. The second is a question of law for local inspector.
1. Is tripping an AFCI a common, known, issue for brand new variable speed blower motors?
2. Question Monday for local electrical inspector: Is AFCI required by law for the furnace?
Still also considering possible amp draw issue. Due to filter being directly against the furnace enclosure, I don’t have a handy place to drill to insert a manometer tap to check pressure rise across the blower. The prior unit had a little length of duct after the filter for inlet pressure and also a handy tapping hole near heat exchanger coils for outlet pressure. So I can’t tell yet if it was too much load on the motor. We’ll have a cold spell this weekend, so if it’s motor load, the new 20A GFI only breaker should trip.
I have found a reference, but it’s AI -not real intelligence, that supports the installers claim:
“High Frequency Capacitive Leakage
Many modern furnaces with variable speed blower motors may not be compatible with AFCIs. They can produce high-frequency electrical noise that triggers the breaker.”
If this is the case, I would have expected it to come up elsewhere in the forum unless it is such common knowledge that no one uses AFCI with a furnace. No mention of it in the furnace installation info.
NFPA 70, NEC 2023 article 210.12 seems to indicate AFCI is required: “AFCI protection shall be installed in accordance with 210.12(B) through (E). In 210.12(B) it lists various rooms, closets, hallways and the catch-all “Similar areas”. No mention of what constitutes a “similar area”. It provides exceptions only for fire alarms and arc welders.
The furnace is in an unfinished basement.
So I have 2 concerns. Only the first applies to this forum. The second is a question of law for local inspector.
1. Is tripping an AFCI a common, known, issue for brand new variable speed blower motors?
2. Question Monday for local electrical inspector: Is AFCI required by law for the furnace?