pbeasley
Senior Member
- Location
- Orange County, CA (for now)
I have been able to get by so far without having problems with AFCI's, but no more. This situation came up over the weekend during trim out and I'm not clear on why this would be the case.
Residence with 200A main panel, 100A sub panel on 2nd floor. Both panels are SqD Homeline. A/C compressors fed from Main panel. There are two 20amp AFCI's (not the combination type) in the sub panel that are tripping, and it appears they trip when the A/C kicks in.
Does it make sense for something up-stream of the breaker to cause this tripping? I am guessing it is more likely a vibration problem but open to other suggestions. No, I don't have a megger, though I may have one soon :smile: ....
Residence with 200A main panel, 100A sub panel on 2nd floor. Both panels are SqD Homeline. A/C compressors fed from Main panel. There are two 20amp AFCI's (not the combination type) in the sub panel that are tripping, and it appears they trip when the A/C kicks in.
Does it make sense for something up-stream of the breaker to cause this tripping? I am guessing it is more likely a vibration problem but open to other suggestions. No, I don't have a megger, though I may have one soon :smile: ....