Installed GFCI breaker--no tripping.
Re-installed the AFCI breaker.
Took apart every connection on the circuit.
Reconnected everything one wire at a time, had my helper turn the breaker on after each re-connection was made. Everything held no problem.
Installed the light fixture (on a 3-way switch) turned breaker on and POP! It tripped.
Removed fixture, installed a pigtail and incandescent light bulb. POP!
Removed the pigtail and light bulb, reset the breaker turned it on and POP!
Installed a regular CH115 breaker, closed the panel, said I would return next week to the customer, got in my truck, and :rant:
I'm at a loss!
You have it tracked down and are very close. Seems to me the problem is associated with the switches. I would disconnect all wires from 3 way devices and start connecting one by one while verifying if afci trips. You had the problem right there in your hands but sometimes it is better to leave then to start ripping stuff apart. Smart man. Also make sure that the light fixture neutral is not spliced in with olanother circuit at the box. Ive seen jobs where neutrals are all spliced together with other circuits. But first, start with device troubleshooting.