afci versus gfci

Status
Not open for further replies.

pnilsson2000

Member
Location
Oregon
I have an older house that has 2 wire outlets thru-out and want to upgrade to 3 wire outlets.
my understanding is that this can be done using a gfci breaker or outlet and labeling the out outlets as gfci protected. well a couple of the rooms are bedrooms and I understand the new code requires afci's in the bedrooms. my question is should I stay with gfci plan or make the bedrooms afci. and if I changed the bedrooms to afci would i still be able to upgrade to 3 wire outlets even if I only two wires at the outlet. it would be very diffucult to add grounds to these outlets. any help would be appericiated
 
Re: afci versus gfci

it is actually my mom's house and yes I am a licensed electrician for the state of oregon.

now that that is out of the way, what do you think?
 
Re: afci versus gfci

If you want to change from two wire to three wire receptacles, you will have to use either GFCI breakers or receptacles and label the receptacles 'GFCI Protected/ No Equipment Ground' as found in 406.3(D)(3)(c).

There is no requirement to make the existing bedroom receptacles AFCI protected. But if you choose to do so, you could:
-use a AFCI breaker and a GFCI receptacle, or
-if your loadcenter is Cutler Hammer, use an AFCI/GFCI breaker.
 
Re: afci versus gfci

GFCI is the best way to allow a 3 wire receptacle to be used on a 2 wire circuit. As far as the AFCI's it may be up to your AHJ. If you had a cb panel there are combo AFCI's GFCI Cb's from one mfg. The 2002 nec requires AFCI's for the entire branch circuit for all dwelling unit bedroom outlets, ie switches, smokes, receptacles
 