shortcircuit2
- South of Bawstin
I have a customer who trips the AFCI breaker when using the Kenmore canister type vacuum which is less than 5 yrs old. The AFCI breakers are newly installed Nov. 2010 and only trip with the vacuum.
I called Eaton (cutler hammer) today and they have many documented problems in the field as many of you can attest to.
So the technician at Eaton informs me of a solution to the problem is to use a surge trap in line with the cord to receptacle connection.
They are mailing one directly to my customer!
Eaton Part #smicro1t
We will see if it works.
shortcircuit
shortcircuit