Do we know that they do?Originally posted by Mattste:
How does an AFCI work?
That is quiet an acomplishment,I commend you for it, my question is, did you test for the master lic. in each state, the reason been I will be doing some electrical volunteer work in Lousiana and was wondering if I could reciprocate with said state.Brad Darnell
Master Electrician
IN-NJ-WI-CT-LA-OH-KY-TX
You probably should have started a new topic for your question.Originally posted by Bill T:
I was directed to this site from EKR.
I have a dedicated circuit for the smoke alarms which according to code is required to be fed from an AFCI breaker. Since the smoke alarms are not grounded does this do any good?
Not really. It's not designed to look for normal "faults" at all, but to sense if any point on the branch circuit is arcing. So if a AFCI circuit breaker senses a arcing pattern in the current flow that it has been programmed to react to, it will trip.Fred wrote:
A GFCI is designed to detect faults between a neutral and ground or hot and ground,but not between hot and neutral. That is the idea behind the AFCI.
That may be what the original sales pitch was to the NFPA, but that does not describe the capabilities of the branch/feeder AFCI we use today. The change in the 2005 code asking for "combination" AFCI's is the NFPA asking for the product they originally thought they were getting.They both protect from respective faults inside the wall as well as cord connected equipment. AFCI basically designed to eliminate fires caused by two wire lamp cords that get frayed behind the bed when it gets to rocking.
That is not correct. 406.3(D) allows GFI protection of existing circuits lacking an EGC, but an AFCI breaker is not the same thing.It also is supposed to provide some sort of protection for other equipment that does not have a ground to facilitate the tripping of a normal breaker.
Not exactly. The AFCI does not driectly act on arcing that would be caused by a loose connection or a single broken wire. That would be a series arc and the arc detection chip in an AFCI does not detect series arcing. The AFCI, may, after a period of time, respond indirectly to the series arc or high resistance fault. It does this only when one or more of the following occur.An AFCI trips on arcing which might occur with loose connections, worn insulation, or carbonized plastic.
Actually, according to Mike Holt's article (linked in my previous post) even the new combination types would not likely trip due to loose connections.Originally posted by rattus:
An AFCI trips on arcing which might occur with loose connections, worn insulation, or carbonized plastic.
Mike Holt:
Although AFCIs have their uses, it's important to note that these protection devices are not designed to prevent fires caused by series arcing at loose connections in devices like switches or receptacles.
Not likely...all switching devices produce series arcing.However, it seems that it would be possible to design a device to detect series arcing. Such a device would be very useful in my opinion.