Judging by the rest of this mess I just wonder what the details of that transformer I see look like.
For the Y-12 Calutrons that enriched uranium in the Manhattan Project they used silver for the coils and busbars because copper was in such short supply (it was needed for brass shells and many other uses).Except for the fact that it tarnishes, silver is supposedly a better conductor than copper... ng).
Fortunately this is not a NEC requirement, it may be a local requirement in some areas, Article 409 still contains 'construction specifications' for allowing us to build them without being subjected to the extraordinary cost of getting 508A listed.2) Custom controls cabinet not listed, or field approved
Hmmmm, a good chunk of the code is written by manufactures, what would they gain by that........Fortunately this is not a NEC requirement, it may be a local requirement in some areas, Article 409 still contains 'construction specifications' for allowing us to build them without being subjected to the extraordinary cost of getting 508A listed.
There seems to be an active campaign to remove 'construction specifications' from the NEC and force us to buy expensive UL standards instead.
Part III. Construction Specifications for 409.100 Enclosures, refers us to Table 110.28, where Note No. 2: (describes) Ingress protection (IP) ratings (from) ANSI/IEC 60529, Degrees of Protection Provided by Enclosures.Fortunately this is not a NEC requirement, it may be a local requirement in some areas, Article 409 still contains 'construction specifications' for allowing us to build them without being subjected to the extraordinary cost of getting 508A listed.
There seems to be an active campaign to remove 'construction specifications' from the NEC and force us to buy expensive UL standards instead.
Now I see it...PFC capacitor. Not required for this area, another extra.Judging by the rest of this mess I just wonder what the details of that transformer I see look like.
Had to save images, and enlarge using image software.
1) Direct buried cables protruding above ground without raceway protection.
2) Custom controls cabinet not listed, or field approved
3) Cabinet raceway missing thread bushings
4) Don't see grounding bus for green wires
Can someone explain those strange looking 2-wire connectors?
Op in #1 made Request for Criticism (RFC), which comes before inspection. The rest was WAGHow do you know that?
I bet it likely is listed..
The larger is a Pump Panel and would meet those requirements. The smaller would as well but is not intended for use as service equipment. It requires a “System Disconnect” ahead of it which usually ends up being the PP.Did not see if op has a control panel label per 409.110 Marking 1-7
I don't see what 410 or 411 have to do with this installation.Your in Nebraska so i dont know what the local NEC requires but
Just looking around the code say further down at;
410.6 Listing Required. "All luminaires, lampholders, and ret-
rofit kits shall be listed."
then
411.4 Listing Required...
There would be a clear indication that 409 panels need to be listed, and that would be a sad day for electricians.
The rural POCO that serves a lot of the area I typically work in does not energize any new service over 250 volts without having a permit/inspection, even otherwise state exempt agriculture services. All the others around here do not do this though.Kwire May have irrigation inspections in his area. Some area POCOs will not provide power unless they are. Anything goes in my area, obviously.
those were examples of articles that require stuff to be listed. As I pointed out a article 409 industrial control panel does not need to be field certified or listed.I don't see what 410 or 411 have to do with this installation.
The panels in question are listed.
Two to six disconnects still will be allowed- they just can't be in the same enclosure or compartment in things like switchboards.I've done the two to six disconnects in the past when I had control of the project start to finish. That will disappear this year with the 20 going into play.. I am the third contractor on this job.