- Location
- Massachusetts
The motor current would not have likely changed, were the manure slurry of uniform consistency.
And what?
Or are you just demonstrating your knowledge of manure?
The motor current would not have likely changed, were the manure slurry of uniform consistency.
By raising the submersible pump to manure slurry level of lower density, its current was brought down to about its full load value and that implies under size pump motor.And what?
OP has indicated that this is new and the media is primarily water up to this point.The motor current would not have likely changed, were the manure slurry of uniform consistency.
OP has indicated that this is new and the media is primarily water up to this point.
One other reason for high current, overload.
Possibly from malfunctions or mistakes in designing/selecting equipment.
I did not look closely, but I believe they are direct drive.I'll repeat, check the gearing. Current will go up as the cube of the RPM's
The propeller pitch also affects the power.I did not look closely, but I believe they are direct drive.
Yes, and that is being investigated.The propeller pitch also affects the power.
The propeller pitch also affects the power.
I had a hunch that was the case.When you said agitator I thought top of tank like Jreaf's photo, not something like those things. I think most thought the same.
That's a new one on me too, never came across something like that. Apparently it's specifically a manure agitator, and the company is from Turkey.
http://www.e-y-s.com/ Click on the little British flag to get the English version.
It's highly unlikely that a sealed one-piece unit like that was not engineered correctly, meaning I doubt the gear ratio or blade pitch is incorrect.
But here's another angle. These things have IEC motors in them, and the literature says that the same unit is good for 230 or 380V 50Hz, or 480V 60Hz (but it would NOT be good for 240V 60Hz). You said in the beginning that it was supposed to pull 21A, and later said it was 15HP. That implies 480V (you didn't say, so I had to deduce).
On that motor, you would have had to connect it in the Star pattern for 480V operation, the nameplate may have said 380V, but it would be the same connections. If you connected it in Delta, the motor is getting low voltage (as far as IT is concerned). The motor equivalent voltage would be 277V, or 58% of what it needs. Torque output would then be very low, about 33% peak torque, even though the speed would be the same. That means as soon as it sees any significant load, slip would increase and it will pull high amps in an attempt to get back to normal speed. When you raise it up and decrease the load, it can do it, but when you lower it, you are overloading it.
Triple check your connections.
That's a new one on me too, never came across something like that. Apparently it's specifically a manure agitator, and the company is from Turkey.
http://www.e-y-s.com/ Click on the little British flag to get the English version.
It's highly unlikely that a sealed one-piece unit like that was not engineered correctly, meaning I doubt the gear ratio or blade pitch is incorrect.
But here's another angle. These things have IEC motors in them, and the literature says that the same unit is good for 230 or 380V 50Hz, or 480V 60Hz (but it would NOT be good for 240V 60Hz). You said in the beginning that it was supposed to pull 21A, and later said it was 15HP. That implies 480V (you didn't say, so I had to deduce).
On that motor, you would have had to connect it in the Star pattern for 480V operation, the nameplate may have said 380V, but it would be the same connections. If you connected it in Delta, the motor is getting low voltage (as far as IT is concerned). The motor equivalent voltage would be 277V, or 58% of what it needs. Torque output would then be very low, about 33% peak torque, even though the speed would be the same. That means as soon as it sees any significant load, slip would increase and it will pull high amps in an attempt to get back to normal speed. When you raise it up and decrease the load, it can do it, but when you lower it, you are overloading it.
Triple check your connections.
Where indeed! I have never heard of a 9 lead IEC motor. I tried the link and didn't get anything of value. I think Jraef just knows stuff.where did you get the literature?
The diagram we were given is for 9 lead delta. The motor is 9 lead. I see no way to change it to wye. I can ohm one out tomorrow to see if it is delta or wye connected internally.
Both.Where indeed! I have never heard of a 9 lead IEC motor. I tried the link and didn't get anything of value. I think Jraef just knows stuff.
Are the leads numbered NEMA style or lettered?
So in the case of the OP he's doomed, there's no way to hook it up other than high or low voltage. There's no way I'd hook it up for low volts and put it on 480V without a factory rep there to throw the switch along with a spare motor in the back of his truck.I didn't see a wiring diagram, I saw a spec sheet that said it was set up for 230, 380, or 460V operation.
If it it a true 9 lead motor, then it's not an IEC. But it might be a 12 lead where they already connected 3 of them internally. It's hard to figure out what some of these IEC mfrs do to be able to sell their products here, I've come across some strange stuff. ......
Turns out another customer in Minnesota has a similar problem, the props are wrong.