difowler44
Member
We installed a 600amp meter rack (three panel boxes and a meterbase supported by 3" posts and unistrut). I tried to upload a picture, but it said the file is too large for the server to process. The AHJ failed it on the inspection for 3 reasons. He wanted me to take off the inner lids for the 3ea outdoor panel boxes so he could view the service wires. It is just one screw for each panel box that is holding the inner lid in place. I guess he didn't have a screw driver.
He also said that I couldn't run the grounding wires from one panel box ground bar to another, cutting the wires and then terminating them at each panel box, and then continuing with a new grounding wire to the next panel box. He wanted me to loop the grounding wire through the grounding lugs on each panel box without cutting the wire.
He also said that I needed 2ea grounding rods (one on each end of the meter rack) instead of just one. I know that you need a ufer ground, and a ground rod at the house, but this is a meter rack that is not attached to the house. It is in a field several yards away from the house.
I believe all of these items aren't necessary according to the code book. Am I correct?
He also said that I couldn't run the grounding wires from one panel box ground bar to another, cutting the wires and then terminating them at each panel box, and then continuing with a new grounding wire to the next panel box. He wanted me to loop the grounding wire through the grounding lugs on each panel box without cutting the wire.
He also said that I needed 2ea grounding rods (one on each end of the meter rack) instead of just one. I know that you need a ufer ground, and a ground rod at the house, but this is a meter rack that is not attached to the house. It is in a field several yards away from the house.
I believe all of these items aren't necessary according to the code book. Am I correct?